No Profanity *** No Flaming *** No Advertising *** No Anti Trappers ***NO POLITICS
No Non-Target Catches *** No Links to Anti-trapping Sites *** No Avoiding Profanity Filter


Home~Trap Talk~ADC Forum~Trap Shed~Wilderness Trapping~International Trappers~Fur Handling

Auction Forum~Trapper Tips~Links~Gallery~Basic Sets~Convention Calendar~Chat~ Trap Collecting Forum

Trapper's Humor~Strictly Trapping~Fur Buyers Directory~Mugshots~Fur Sale Directory~Wildcrafting~The Pen and Quill

Trapper's Tales~Words From The Past~Legends~Archives~Kids Forum~Lure Formulators Forum~ Fermenter's Forum


~~~ Dobbins' Products Catalog ~~~


Minnesota Trapline Products
Please support our sponsor for the Trappers Talk Page - Minnesota Trapline Products


Print Thread
Hop To
Another HVAC question. #6129963
01/18/18 06:35 PM
01/18/18 06:35 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
Beginning to hate old houses!!!!!!!!!!!

The electronic thermostat on the wall is set at 70 Degrees from 8 am to 11 PM. After 11 PM, the Thermostat is set to 68 Degrees. During either set temp, once it reached 68 at night or 70 during the day. The temperature in the house stays at that temp. That's a good thing.

The part I don't get, is why the Boiler turns on every 5 to 6 minutes , when the Temperature on the wall thermostat did not go below either 68 or 70 Degrees ?

One thing I did notice, when I went in the Basement to check the Boiler, that Temperature gauge on the Boiler would go down after the boiler shut off. That is understandable. But, even if the water temp in the Boiler went down to , say 80 Degrees, for example; if the room temp that the wall thermostat reads does not drop below what it was set at; why would the Boiler fire up ?

Re: Another HVAC question. [Re: Canvasback2] #6129968
01/18/18 06:37 PM
01/18/18 06:37 PM
Joined: Jul 2016
Posts: 5,518
South Carolina
T
Tom cat Offline
trapper
Tom cat  Offline
trapper
T

Joined: Jul 2016
Posts: 5,518
South Carolina
Is your thermostat ok??


Sugarcreektrapping@gmail.com
Re: Another HVAC question. [Re: Canvasback2] #6129979
01/18/18 06:43 PM
01/18/18 06:43 PM
Joined: Sep 2015
Posts: 749
Broome NY . not the city
greenetrapper Offline
trapper
greenetrapper  Offline
trapper

Joined: Sep 2015
Posts: 749
Broome NY . not the city
Your boiler is set up to maintain temperature. That's what it sounds like to me. You can get a new aquastat that will only bring your boiler on when is a call for heat.

Re: Another HVAC question. [Re: Canvasback2] #6129982
01/18/18 06:45 PM
01/18/18 06:45 PM
Joined: Sep 2015
Posts: 749
Broome NY . not the city
greenetrapper Offline
trapper
greenetrapper  Offline
trapper

Joined: Sep 2015
Posts: 749
Broome NY . not the city
even if you're boiler set up to maintain temperature. It should not be coming on that often. Are you sure there's not a pump running somewhere where you are dispersing Heat

Last edited by greenetrapper; 01/18/18 06:45 PM.
Re: Another HVAC question. [Re: Canvasback2] #6129983
01/18/18 06:45 PM
01/18/18 06:45 PM
Joined: Oct 2017
Posts: 578
Wisconsin
V
virgil1972 Offline
trapper
virgil1972  Offline
trapper
V

Joined: Oct 2017
Posts: 578
Wisconsin
It sounds like a it is working like it is supposed to. It comes on a maintains the temperature in the house.

Re: Another HVAC question. [Re: Canvasback2] #6129991
01/18/18 06:58 PM
01/18/18 06:58 PM
Joined: Jul 2016
Posts: 3,928
NY
Canvasback2 Offline OP
trapper
Canvasback2  Offline OP
trapper

Joined: Jul 2016
Posts: 3,928
NY
Starts up and runs for 5 or 6 minutes and shuts down for 5 or 6 minutes. Then on again. If the temp in the house went down, I could understand it going back on. But, it doesn't drop one degree below set temp. The old Boiler and old wall thermostat when set to 70. would turn on at 68 and turn off at either 70 or 71.

Re: Another HVAC question. [Re: Canvasback2] #6130003
01/18/18 07:10 PM
01/18/18 07:10 PM
Joined: Feb 2007
Posts: 1,193
Goldsboro, NC
John C Offline
trapper
John C  Offline
trapper

Joined: Feb 2007
Posts: 1,193
Goldsboro, NC
Ok. The temperature differential setting is to tight. It should be user adjustable on a Honeywell aqua stat via a dial on the side exposed when you remove the Grey cover. Say your aqua stat is set to 150 degrees. At 150 it will cut off. When temps drop below 150 it will cut on. With the differential set to say 5 degrees it will cut off at 150 and then on again at 145. This keeps it from short cycling. Play around with it and see how a 10 or 15 or 20 degree differential works out. Some of the Honeywell aqua stats are adjustable from 3 degrees to 35 degrees.


More Cowbell
Re: Another HVAC question. [Re: Canvasback2] #6130149
01/18/18 08:50 PM
01/18/18 08:50 PM
Joined: Mar 2014
Posts: 1,324
vermont
V
vermontster Offline
trapper
vermontster  Offline
trapper
V

Joined: Mar 2014
Posts: 1,324
vermont
Canvasback i would see if your check vale is stuck open allowing the water to move thru out the system. Is the thermostat something. If so make sure its not programmed as a heatpump. you can tap on the check valve with a hammer to make it close.


The bitterness of poor quality last a lot longer than the sweetness of low price
Re: Another HVAC question. [Re: Canvasback2] #6132119
01/20/18 04:11 PM
01/20/18 04:11 PM
Joined: Mar 2014
Posts: 1,324
vermont
V
vermontster Offline
trapper
vermontster  Offline
trapper
V

Joined: Mar 2014
Posts: 1,324
vermont
Canvasback2 what did you find out with your boiler?


The bitterness of poor quality last a lot longer than the sweetness of low price
Re: Another HVAC question. [Re: Canvasback2] #6132158
01/20/18 04:53 PM
01/20/18 04:53 PM
Joined: Aug 2012
Posts: 581
clinton county Mi.
S
slicktail Offline
trapper
slicktail  Offline
trapper
S

Joined: Aug 2012
Posts: 581
clinton county Mi.
Do you have zones?? Maybe another thermostat someplace else in the house calling for heat?


MTPC
NTA
FTA
NRA
Till I Drop
Re: Another HVAC question. [Re: virgil1972] #6132176
01/20/18 05:27 PM
01/20/18 05:27 PM
Joined: Feb 2014
Posts: 13,157
Ky
J
jbyrd63 Offline
trapper
jbyrd63  Offline
trapper
J

Joined: Feb 2014
Posts: 13,157
Ky
Originally Posted By: virgil1972
It sounds like a it is working like it is supposed to. It comes on a maintains the temperature in the house.


X2 Welcome to the age of electronics. I put a new heat unit in which came with a new electronic thermostat . Bout drove me nuts first week. Doing same thing. I called the furnace guy and he said the new stats "check " the air on occasion . But the air handler has to be running. Old mercury stats never did that.

Re: Another HVAC question. [Re: Canvasback2] #6132190
01/20/18 05:51 PM
01/20/18 05:51 PM
Joined: Mar 2014
Posts: 1,324
vermont
V
vermontster Offline
trapper
vermontster  Offline
trapper
V

Joined: Mar 2014
Posts: 1,324
vermont
I still think it a open check valve or a open zone valve. Either one allows for convection or even gravity to constantly move the hot water to the base board. Then it cools and moves back to the boiler nonstop. The boiler final cools enough and turns back on and reheats the water. All the time on cold days acts normal but on warmer days can over heat the space. I have seen this a lot times.


The bitterness of poor quality last a lot longer than the sweetness of low price