Re: New furnace is junk. [Re: 1lessdog] #8051871
01/16/24 08:48 PM
01/16/24 08:48 PM
Joined: Jan 2012
Posts: 1,640
Warren co Mo
H
hrdtoflw Offline
trapper
hrdtoflw  Offline
trapper
H

Joined: Jan 2012
Posts: 1,640
Warren co Mo
Could they have not opened all valves properly. I have an electric boiler system, with base board radiators. I also have an outdoor wood burner that heats the system, and bypasses the electric boiler, but uses the same pump. The valve opening and closing can be quite confusing. We bought this home last year, and luckily, the previous owner had all valves tagged with instructions.
The installer should be there getting the new equipment working properly, or replacing it!!!


If your mind draws a blank, turn off the sound, because ya can't learn a thing if you're doin all the talkin
Re: New furnace is junk. [Re: 1lessdog] #8051874
01/16/24 08:50 PM
01/16/24 08:50 PM
Joined: Oct 2017
Posts: 43
North Dakota
Torman Offline
trapper
Torman  Offline
trapper

Joined: Oct 2017
Posts: 43
North Dakota
You can try turning the silver screw on the pump and if water comes out its typically circulating. You can manually open those zone valves on the side. Another thing would be if they crossed up one of the thermostat wires with the wrong zone.

Re: New furnace is junk. [Re: 1lessdog] #8051878
01/16/24 08:53 PM
01/16/24 08:53 PM
Joined: Mar 2014
Posts: 921
Ontario, Canada
S
sweetwilliam Offline
trapper
sweetwilliam  Offline
trapper
S

Joined: Mar 2014
Posts: 921
Ontario, Canada
Are those some kind of a compression joint on the pipes? Have seen a lot of problems with the welded joints in New pvc pipes with over compressing the joint and restricting water flow.

Re: New furnace is junk. [Re: 1lessdog] #8051879
01/16/24 08:54 PM
01/16/24 08:54 PM
Joined: Jan 2020
Posts: 4,954
Aliceville, Kansas 43
Yukon John Offline
trapper
Yukon John  Offline
trapper

Joined: Jan 2020
Posts: 4,954
Aliceville, Kansas 43
Looks to me like you need to raise some Cain with the install company. I personally would not be very pleasing to deal with if it were me.


Act like a blank, get treated like a blank. Insert your own blank!
Re: New furnace is junk. [Re: 1lessdog] #8051881
01/16/24 08:54 PM
01/16/24 08:54 PM
Joined: Mar 2018
Posts: 2,239
Missouri
H
HayDay Offline
trapper
HayDay  Offline
trapper
H

Joined: Mar 2018
Posts: 2,239
Missouri
That gray cannister, lower left corner isn't bleeding anything. It's the expansion tank. The shock absorber in the system. Bleeder vents may be upstairs. Look for a screw on a riser on each fin tube. Crack those open to see if you get water or air.

Re: New furnace is junk. [Re: sweetwilliam] #8051883
01/16/24 08:56 PM
01/16/24 08:56 PM
Joined: Feb 2007
Posts: 673
N. Dakota
1
1lessdog Offline OP
trapper
1lessdog  Offline OP
trapper
1

Joined: Feb 2007
Posts: 673
N. Dakota
Originally Posted by sweetwilliam
Are those some kind of a compression joint on the pipes? Have seen a lot of problems with the welded joints in New pvc pipes with over compressing the joint and restricting water flow.



Yes everything is compression fittings.

Re: New furnace is junk. [Re: 1lessdog] #8051886
01/16/24 08:57 PM
01/16/24 08:57 PM
Joined: Oct 2017
Posts: 43
North Dakota
Torman Offline
trapper
Torman  Offline
trapper

Joined: Oct 2017
Posts: 43
North Dakota
Another idea would be if they crossed up a supply with a return and it's short cycling thru the boiler. It's seems like there is too many zones on a single pump.

Re: New furnace is junk. [Re: 1lessdog] #8051897
01/16/24 09:07 PM
01/16/24 09:07 PM
Joined: Feb 2007
Posts: 673
N. Dakota
1
1lessdog Offline OP
trapper
1lessdog  Offline OP
trapper
1

Joined: Feb 2007
Posts: 673
N. Dakota
I would like to find a real sharp guy that can trouble shoot the problem. And take the installer to court. Because there in no hurry to come back.

Re: New furnace is junk. [Re: 1lessdog] #8051908
01/16/24 09:15 PM
01/16/24 09:15 PM
Joined: Feb 2021
Posts: 2,365
Interior Alaska
O
Oh Snap Offline
trapper
Oh Snap  Offline
trapper
O

Joined: Feb 2021
Posts: 2,365
Interior Alaska
Can you hear gurgling in the lines. That would indicate running in the wrong direction but wouldn't cause poor heat. Are there bleeder valves in the highest part of the system or is the bladder tank (gray one) where the auto bleeder is?

You probably are air locked!

Last edited by Oh Snap; 01/16/24 09:16 PM.

I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
Re: New furnace is junk. [Re: 1lessdog] #8051937
01/16/24 09:40 PM
01/16/24 09:40 PM
Joined: Oct 2017
Posts: 43
North Dakota
Torman Offline
trapper
Torman  Offline
trapper

Joined: Oct 2017
Posts: 43
North Dakota
The brass fitting on top of your expansion tank it a super vent. Make sure the little cap is loose on it to allow air to come out. I have had a faulty one of those, you can take a small wire or paper clip and insert it thru the small hole behind the cap. Just push a little bit and water will squirt out of it along with air. They should have installed that before the pump.

Re: New furnace is junk. [Re: 1lessdog] #8051953
01/16/24 09:54 PM
01/16/24 09:54 PM
Joined: Feb 2021
Posts: 2,365
Interior Alaska
O
Oh Snap Offline
trapper
Oh Snap  Offline
trapper
O

Joined: Feb 2021
Posts: 2,365
Interior Alaska
Is the fin tube fed from below? You said in an earlier post that the pipes on each side of the fin tube were hot but the fin tube was cool. If fed from below the water could be air blocked in the fin tube and trickling through and the pipes on each side be holding water thus be hot.


I love the smell of burning spruce---I love the sound of a spring time goose---I love the feel of 40 below---from my trapline I will never go!
Re: New furnace is junk. [Re: 1lessdog] #8051970
01/16/24 10:06 PM
01/16/24 10:06 PM
Joined: Oct 2009
Posts: 7,444
western mn
B
bucksnbears Offline
trapper
bucksnbears  Offline
trapper
B

Joined: Oct 2009
Posts: 7,444
western mn
Gotta ask..., what made you buy a fuel oil one?


swampgas chili and schmidt beer makes for a deadly combo

You have to remember that 1 out of 3 Democratic Voters is just as dumb as the other two.
Re: New furnace is junk. [Re: 1lessdog] #8051979
01/16/24 10:15 PM
01/16/24 10:15 PM
Joined: Nov 2017
Posts: 11,329
Maine, Aroostook
Posco Offline
trapper
Posco  Offline
trapper

Joined: Nov 2017
Posts: 11,329
Maine, Aroostook
Try manually opening the zone valves.

Re: New furnace is junk. [Re: 1lessdog] #8051993
01/16/24 10:23 PM
01/16/24 10:23 PM
Joined: Jan 2007
Posts: 1,004
Eastern Shore, MD
J
JoMiBru Offline
trapper
JoMiBru  Offline
trapper
J

Joined: Jan 2007
Posts: 1,004
Eastern Shore, MD
Do you have a pressure gauge on the propane line? Low temps affect pressures. I know this from our lp corn dryer ( grain dryer ). Maybe an orfice is plugged or not working properly? Did they switch it from natural gas to propane like a gas stove, and was it done correct?

I’m no hvac guy, but I’d hold the company who would installed the unit responsible.

Good luck hopefully your issue is resolved.

Re: New furnace is junk. [Re: 1lessdog] #8052011
01/16/24 10:36 PM
01/16/24 10:36 PM
Joined: Nov 2017
Posts: 11,329
Maine, Aroostook
Posco Offline
trapper
Posco  Offline
trapper

Joined: Nov 2017
Posts: 11,329
Maine, Aroostook
If your boiler temp is reaching 180 degrees, that's not the issue. It's a circulation issue.

Re: New furnace is junk. [Re: 1lessdog] #8052062
01/16/24 11:11 PM
01/16/24 11:11 PM
Joined: Apr 2007
Posts: 2,320
venango county,pennslyvania
minklessinpa Offline
trapper
minklessinpa  Offline
trapper

Joined: Apr 2007
Posts: 2,320
venango county,pennslyvania
just a thought, what is that circ pump rated at? and is it installed right? should be a arrow on the body showing direction of flow.


life member Pennsylvania trappers
life member vfw
member fta
Re: New furnace is junk. [Re: 1lessdog] #8052183
01/17/24 06:45 AM
01/17/24 06:45 AM
Joined: Apr 2012
Posts: 2,981
new york
M
mike mason Offline
trapper
mike mason  Offline
trapper
M

Joined: Apr 2012
Posts: 2,981
new york
My set up is similar to yours. I isolate one zone and purge the air, get that zone working properly and go to the 2nd zone, then the 3rd. I have circulators on each zone.

Re: New furnace is junk. [Re: 1lessdog] #8052194
01/17/24 07:06 AM
01/17/24 07:06 AM
Joined: Feb 2015
Posts: 165
Mn
R
Reaperman Offline
trapper
Reaperman  Offline
trapper
R

Joined: Feb 2015
Posts: 165
Mn
I have Taco brand pumps which have an arrow on the housing that shows the flow direction, perhaps yours does also. It’s not real visible because the arrow is molded into the housing and painted over.

Re: New furnace is junk. [Re: 1lessdog] #8052218
01/17/24 08:17 AM
01/17/24 08:17 AM
Joined: Dec 2006
Posts: 291
PA
S
scrapper Offline
trapper
scrapper  Offline
trapper
S

Joined: Dec 2006
Posts: 291
PA
I bet the loops are air locked. You may have to install purge valves at the boiler to get the water to circulate.

Re: New furnace is junk. [Re: 1lessdog] #8052251
01/17/24 09:12 AM
01/17/24 09:12 AM
Joined: Dec 2008
Posts: 3,907
eastern WV
R
Ridge Runner1960 Offline
trapper
Ridge Runner1960  Offline
trapper
R

Joined: Dec 2008
Posts: 3,907
eastern WV
manually open the zone valves and see what you get